I am trying to calculate ampacity rating of direct buried cables. The thermal resistivity used significantly impacts the rating of these cables.
I have a report where they have performed a thermal resistivity test of the soil. It appears as if they have put the soil in an oven (or similar) and measured both the thermal conductivity (W/mK) and resistivity (mK/W) over time. The results are tabulated and continue until the moisture content of the soil is 0% (4 points are measured with moisture contents of 30.24%, 25.13%, 8.89% and 0%). The conductivity results vary from 1 to 0.2 and resistivity from 0.7 to 2.3 (in that order with relation to moisture content).
The cables will have bedding sand around them to protect them mechanically, but above this the intent will be to backfill with natural spoil.
What thermal resistivity do you use with the ampacity calculations?
IEC-60287-11 talks about this, but the rules only apply to isolated cables. There are multiple cables in this trench.
I am trying to calculate ampacity rating of direct buried cables. The thermal resistivity used significantly impacts the rating of these cables.
I have a report where they have performed a thermal resistivity test of the soil. It appears as if they have put the soil in an oven (or similar) and measured both the thermal conductivity (W/mK) and resistivity (mK/W) over time. The results are tabulated and continue until the moisture content of the soil is 0% (4 points are measured with moisture contents of 30.24%, 25.13%, 8.89% and 0%). The conductivity results vary from 1 to 0.2 and resistivity from 0.7 to 2.3 (in that order with relation to moisture content).
The cables will have bedding sand around them to protect them mechanically, but above this the intent will be to backfill with natural spoil.
What thermal resistivity do you use with the ampacity calculations?
IEC-60287-11 talks about this, but the rules only apply to isolated cables. There are multiple cables in this trench.