prichmon
Mechanical
- Oct 5, 2010
- 32
We are looking at replacing a Cooling tower with Geothermal Cooling for a process water loop.
80KW total power usage.
10*F temp differential on cooling tower design
20*F temp design differential on system
operating pressure 30psi
If we move to geothermal cooling our temp differential will be ~35*F+ due to ground water typically not exceeding 60*F. The thought is to simplify the system by elimination of the HX, cooling tower and tanks.
Based on copper pipe of thermal transfer of 13.11 W/M^2*K; PE pipe 7.09 W/m^2*K
1" copper tubing
10*F differential copper equates to ~4595 feet pipe
35*F differential copper equates to ~1315' pipe
Based on data on ground temperature changes the loops need to be ~20' deep to minimize temp swings to the +/-10* range.
I would appreciate if someone with experience in this area could assist me?
Thank you
Rich