SindhuK
Electrical
- Oct 22, 2014
- 7
Hello Everyone,
I have a 3MVA 34.5kV/480V Y-Y solid ground transformer, the primary and secondary neutral terminals are tied together and grounded near the transformer. The primary cable from the 34.5kV switchgear feeder is 4/0AWG 3-wire (no neutral wire). On 480V side I have a switchboard with 4000A main and 2500 A feeder breakers LSIG type with ground fault protection feature.
My questions are:
1] Does the high side ground fault relay need to be time coordinated with low-side 480V breaker ground fault curves?
2] How does the primary side relays see the ground faults on 480V bus, as a phase fault or as a ground fault ?
3] Not having a neutral connection between high side switchgear and the transformer primary, will effect the zero sequence current flow?
Thanks in advance.
I have a 3MVA 34.5kV/480V Y-Y solid ground transformer, the primary and secondary neutral terminals are tied together and grounded near the transformer. The primary cable from the 34.5kV switchgear feeder is 4/0AWG 3-wire (no neutral wire). On 480V side I have a switchboard with 4000A main and 2500 A feeder breakers LSIG type with ground fault protection feature.
My questions are:
1] Does the high side ground fault relay need to be time coordinated with low-side 480V breaker ground fault curves?
2] How does the primary side relays see the ground faults on 480V bus, as a phase fault or as a ground fault ?
3] Not having a neutral connection between high side switchgear and the transformer primary, will effect the zero sequence current flow?
Thanks in advance.