BadgerPE
Structural
- Jan 27, 2010
- 500
I am working on my first building design in which composite action is used between the steel framing and the concrete deck. Governing codes are IBC 2009/AISC 13th. Currently, I have the building modeled using RISA Floor and I am working to verify results by hand of a few of the girders/beams. My question is related to the placement of shear studs for a girder subjected to point loads. Please see attached document for two cases I am considering (diagrams are arbitrary and are assuming SIGMA_Qn are the same for each girder).
General considerations:
f'c=4 ksi
Deck = 18 ga 2" deep
Overall slab thickness = 6.5"
Shear stud diameter = 0.75"
Case 1:
Girder subject to 3 point loads of approximately equal magnitude.
The way I understand section I3.2d.(6) of AISC is that I should have the full amount of shear studs, required to develop the moment at the concentrated load, from the concentrated load to the point of zero moment. In between the two outside concentrated loads shear studs should be spaced at the min(8t, 36"). This seems to be pretty straight forward and it is how RISA calculates the shear studs.
Case 2:
Girder is subjected to 6 concentrated loads of varying magnitude.
This is where I get a little confused. I am still applying multiple concentrated loads to the girder. However, RISA provides shear studs at uniform spacing across the entire member. Is there something in the code/DG that provides this method of stud distribution? About the only thing that I see is in Comm I3.2d.(6) the first paragraph reads "Uniform spacing of shear connectors is permitted, except in the presence of heavy concentrated loads." I take it RISA's interpretation of this is that when you increase the number of concentrated loads, you start to get away from the "heavy concentrated loads" segment of the Comm because the loading is more spread out on the girder than when there are only 2-3 loading points.
After re-reading the Comm and typing this up, it makes more sense in my head. Can anyone verify that this is the approach they would take? Also, how many point loads on a girder would it take to go from stud spacing as indicated in Case 1 to stud spacing in Case 2?
Thanks!
General considerations:
f'c=4 ksi
Deck = 18 ga 2" deep
Overall slab thickness = 6.5"
Shear stud diameter = 0.75"
Case 1:
Girder subject to 3 point loads of approximately equal magnitude.
The way I understand section I3.2d.(6) of AISC is that I should have the full amount of shear studs, required to develop the moment at the concentrated load, from the concentrated load to the point of zero moment. In between the two outside concentrated loads shear studs should be spaced at the min(8t, 36"). This seems to be pretty straight forward and it is how RISA calculates the shear studs.
Case 2:
Girder is subjected to 6 concentrated loads of varying magnitude.
This is where I get a little confused. I am still applying multiple concentrated loads to the girder. However, RISA provides shear studs at uniform spacing across the entire member. Is there something in the code/DG that provides this method of stud distribution? About the only thing that I see is in Comm I3.2d.(6) the first paragraph reads "Uniform spacing of shear connectors is permitted, except in the presence of heavy concentrated loads." I take it RISA's interpretation of this is that when you increase the number of concentrated loads, you start to get away from the "heavy concentrated loads" segment of the Comm because the loading is more spread out on the girder than when there are only 2-3 loading points.
After re-reading the Comm and typing this up, it makes more sense in my head. Can anyone verify that this is the approach they would take? Also, how many point loads on a girder would it take to go from stud spacing as indicated in Case 1 to stud spacing in Case 2?
Thanks!