KJ7
Mechanical
- Nov 3, 2011
- 6
Hi all,
My question is more fundamental than anything else, but it seems like I am really missing something here.
We are installing a globe valve as the one shown in the attached image in a 2” NPS piping line. The current piping design does not call for any supports assuming the piping will withstand the weight and the force of the valve. In attempts to figure out how much the piping will displace under the force exerted by the valve actuator as the valve operates we came out with a vector force of 10000 lbf generated by the actuator and transferred to the stem and the valve body. As you can imagine with 10000 lbf of force the piping around the valve deflects more than 0.25” and it fails code requirements.
We came out with 10000 lbf from the effective are of the pneumatic actuator and the air pressure requirements. The actuator is 17” in diameter and it is actuated with 50-80 psi of air. The valve is normally closed therefore the energy is stored in the springs in form of potential energy. Now… as the valve closes the potential energy, as I understand it, is used to overcome pressure and provide seating force needed to provide sealing. For the sake of argument lets assume the valve will be closing against 0 pressure, which will be the worst case scenario since there will be no damping of the closing.
I am to apply a point load at the center of the valve what do you think this value should be? The 10000 lbf of force it seems too high but I can NOT come out with a logical explanation of why it should be something else and what that value might be…
We are applying it as a static force considering the valve will be closing in 1-2 seconds.
Thank you for reading and have a good day!
KJ7
My question is more fundamental than anything else, but it seems like I am really missing something here.
We are installing a globe valve as the one shown in the attached image in a 2” NPS piping line. The current piping design does not call for any supports assuming the piping will withstand the weight and the force of the valve. In attempts to figure out how much the piping will displace under the force exerted by the valve actuator as the valve operates we came out with a vector force of 10000 lbf generated by the actuator and transferred to the stem and the valve body. As you can imagine with 10000 lbf of force the piping around the valve deflects more than 0.25” and it fails code requirements.
We came out with 10000 lbf from the effective are of the pneumatic actuator and the air pressure requirements. The actuator is 17” in diameter and it is actuated with 50-80 psi of air. The valve is normally closed therefore the energy is stored in the springs in form of potential energy. Now… as the valve closes the potential energy, as I understand it, is used to overcome pressure and provide seating force needed to provide sealing. For the sake of argument lets assume the valve will be closing against 0 pressure, which will be the worst case scenario since there will be no damping of the closing.
I am to apply a point load at the center of the valve what do you think this value should be? The 10000 lbf of force it seems too high but I can NOT come out with a logical explanation of why it should be something else and what that value might be…
We are applying it as a static force considering the valve will be closing in 1-2 seconds.
Thank you for reading and have a good day!
KJ7