good day every one i have simple
Ma.ahmed
6
good day every one
i have simple structure it is small warehouse with dimensions 9.6x4 and Hight is 6m
it has one wall side fully opened 9.6x6=57.6m2
other openings in other walls = 9.6*2.1+4*2.1*2=40m2
my question is
is this structure classified as opened or partially enclosed?
and if wind hit the structure in direction of opened wall shall i consider opened structure in this direction, or all structure will be partially enclosed
Regardless of code, I personally would be designing it as if enclosed for lateral and whichever type produces the worst uplift. Essentially penalizing myself as much as possible. On a structure this small it likely has very little increase in member sizing, and should expediate your design time.
I haven't read up on this in a while, but I'm pretty sure partially enclosed is the most severe loading condition due to the increased internal pressure.
This article gives good insight on the enclosure class.
 https://files.engineering.com/getfile.aspx?folder=2f35bee0-60ce-4edf-94c8-f45f76c0b161&file=ASCE_7-16_Open,_Enclosed_Partially_Enclosed_Classification.pdf