chumet1
Mechanical
- Feb 6, 2013
- 40
governor valve positioner link stud fractured at the point where the link is joined to the governor actuator. i measured the vertical vibrations on the position shown on the picture attached on different units (units 6 & 7) because they have the same valve design and unit capacity. on unit 6, the one with the fractured link the vibrations were 19mm/s whilst at unit 7 were 13mm/s. we replaced the mild steel stud with a high tensile steel stud and it also broke in 2days i think due to its brittleness. due to the ripped threads we installed an 8mm mild steel thread that is holding on for now. my question is what is the allowable vibration at the governor valve for a 150MW capacity unit and what are the likely causes of these vibrations from your experience. and also possible corrective actions to solve this problem because i believe our solution is just a stop gap measure.