Horizontal bracing is a good idea as long as there are no conflicts with ducts that come out the bottom of the unit. Sometimes they come out the side of the unit, but more often they come out the bottom. If there would be a conflict, I would then design the beams to handle biaxial bending like whyun says and omit horizontal bracing. This gives you heavier beams, but it's also easier to erect. I use knee braces on the posts, but you have to keep the work point at the bottom of the brace up far enough so that the roof penetration can be flashed with a boot. Also, if your framing will be hot dipped galvanized bolted connections are prefered because welding through zinc is not recommended (although doable).
I assume this is a rooftop platform that you are doing. If my assumption is correct, another consideration is the height of the platform above the roof. You should leave enough space between the bottom of the platform and the roof surface so that when it's time to re-roof, workers can reasonably work under the platform to put the new roof down. Depending on the size of the platform, roughly 3 feet is good. This could be less for a small platform.