AntoineCham
Mechanical
- Dec 22, 2023
- 3
Greetings,
I have a high rise hotel where fire flow is requested to be 1500 gpm while standpipe demand is 1000 gpm. The required minimum pressure for the hydrants (1500 gpm) is 20 psi and for the stanpipe is 225 psi. The designer selected a fire pump of 1500 gpm at 225 psi. I guess this system is oversized. My proposal is to change the pump into 1000 gpm @ 225 psi. Also the water tanks if sized at 1500 gpm for 2 hours is giving 680 cu.m. Figures are huge. Any advice...
Regards,
I have a high rise hotel where fire flow is requested to be 1500 gpm while standpipe demand is 1000 gpm. The required minimum pressure for the hydrants (1500 gpm) is 20 psi and for the stanpipe is 225 psi. The designer selected a fire pump of 1500 gpm at 225 psi. I guess this system is oversized. My proposal is to change the pump into 1000 gpm @ 225 psi. Also the water tanks if sized at 1500 gpm for 2 hours is giving 680 cu.m. Figures are huge. Any advice...
Regards,