Ground cable size required for MV circuit
I am currently designing a power system to use 3 1/C 500 kcmil MV cables. I am doing a calculation to determine the size of conduit required as well as grounding cable size required.
I found thread on forum listed here about grounding cable size required:
thread238-502586: Sizing an equipment grounding conductor for high voltage in duct bank
Is this part of that thread correct for sizing ground cable on anything over 1000 Volts?
7anoter4 (Electrical)20 Feb 23 12:26
See NEC
Part X. Grounding of Systems and Circuits of over 1000 Volts
250.190 Grounding of Equipment
(C) Equipment Grounding Conductor
(3) Sizing. Equipment grounding conductors shall be sized in
accordance with Table 250.122 based on the current rating of
the fuse or the overcurrent setting of the protective relay
See also:
IEEE 142/2007 2.7.4.4 Equipment grounding conductor sizing
If correct, why do they call it equipment grounding conductor? Wouldn't it just be grounded conductor? when I think of equipment grounding conductor I think cable to ground Xfmr panels, sgear panels or any other equipment exterior to electrical room or substation ground. What am I missing here?
I am currently designing a power system to use 3 1/C 500 kcmil MV cables. I am doing a calculation to determine the size of conduit required as well as grounding cable size required.
I found thread on forum listed here about grounding cable size required:
thread238-502586: Sizing an equipment grounding conductor for high voltage in duct bank
Is this part of that thread correct for sizing ground cable on anything over 1000 Volts?
7anoter4 (Electrical)20 Feb 23 12:26
See NEC
Part X. Grounding of Systems and Circuits of over 1000 Volts
250.190 Grounding of Equipment
(C) Equipment Grounding Conductor
(3) Sizing. Equipment grounding conductors shall be sized in
accordance with Table 250.122 based on the current rating of
the fuse or the overcurrent setting of the protective relay
See also:
IEEE 142/2007 2.7.4.4 Equipment grounding conductor sizing
If correct, why do they call it equipment grounding conductor? Wouldn't it just be grounded conductor? when I think of equipment grounding conductor I think cable to ground Xfmr panels, sgear panels or any other equipment exterior to electrical room or substation ground. What am I missing here?