Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Ground fault on Wye side of Delta-Wye Transformer with grounded Wye Secondary 2

Status
Not open for further replies.

Ollie94

Electrical
Sep 30, 2020
4
When a ground fault occurs on the secondary side of a Delta/Wye Transformer which has it’s Wye secondary grounded, how does the Primary see it as a phase to phase fault?
 
Replies continue below

Recommended for you

Draw out the transformer windings and the current flows. Amp*turn balance must be maintained for each winding; if there's current on one side, there has to be current on the other side, likewise if there's no current on one side then there's no current on the other side.
 
Ah right thanks, that makes more sense. What would happen if phase A had an SLG fault on the grounded Wye secondary? Would it appear to be a phase to phase fault between phase A and phase B? And for an SLG fault on phase B it would appear to be a phase to phase fault between phase B and phase C on the Delta primary?
 
It depends on the transformer vector group.
If vector group is Dyn1, SLG fault in r-phase on secondary will have currents in R&B phases on Primary. If Dyn11, it will be in R&Y phases.
If you had done vector group test on transformer, it would be easy to appreciate.
 
That’s cleared things up. Thanks for the explanation.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor