Owameng
Electrical
- Jun 20, 2023
- 1
Hi to everyone!
An industrial facility privately owns a 34.5 kV overhead distribution line that supplies several motors for their main operation. Now, they are planning to add 2 large water pumps (440V, 100 hp, 3-phase each) and also want to provide single phase power for premise lighting and small office.
I have drafted my design and decided that I will propose a bank of 34.5 kV - 440V, step down transformers which are wye-connected on the secondary to energize a panel with 3 branches - two 3 pole breakers for water pumps and one 2 pole breaker that will feed a 440V - 230V small, single phase, step-down transformer for lighting and office loads. Finished.
However, as part of learning, I am curious about something. Considering that single phase loads are pretty small compared to three phase pump loads, I am thinking what if instead of a wye-connected secondary transformer bank, I propose a delta-connected secondary with high-leg? This will give me 440V for the pumps and 220V for the single phase loads.
I have few issues though. First, delta high-leg is not a common transformer connection from where I live. I think I've never heard it yet on the field though I am still a young engineer with limited experience. Second, in wye-connected, I can easily have ground-fault protection for the water pump. I can run an EGC to bond the motor metal casing with branch circuit enclosure and with the GEC at the main service disconnect. I don't think I have this liberty on delta high leg. As I see it, these three phase water pumps will be fed by an ungrounded delta source. Thus, I believe that an intricate and dedicated ground fault detection and isolation is recommended on each of these pumps.
Have you experienced the same situation? What did you do? Do you think it is better to stick with my drafted design (and purchase a separate small single phase step down transformer for single phase loads)? Or connecting to a high leg delta plus individual ground fault protection is worth it? What are your proposed ground fault protection and detection on this scenario?
I want to learn from your experiences. Consider me your youngest brother on this family and my question is solely out of curiosity and knowledge sharing. I don't intend to replace my current design without proper training.
Thank you for your time and knowledge.
An industrial facility privately owns a 34.5 kV overhead distribution line that supplies several motors for their main operation. Now, they are planning to add 2 large water pumps (440V, 100 hp, 3-phase each) and also want to provide single phase power for premise lighting and small office.
I have drafted my design and decided that I will propose a bank of 34.5 kV - 440V, step down transformers which are wye-connected on the secondary to energize a panel with 3 branches - two 3 pole breakers for water pumps and one 2 pole breaker that will feed a 440V - 230V small, single phase, step-down transformer for lighting and office loads. Finished.
However, as part of learning, I am curious about something. Considering that single phase loads are pretty small compared to three phase pump loads, I am thinking what if instead of a wye-connected secondary transformer bank, I propose a delta-connected secondary with high-leg? This will give me 440V for the pumps and 220V for the single phase loads.
I have few issues though. First, delta high-leg is not a common transformer connection from where I live. I think I've never heard it yet on the field though I am still a young engineer with limited experience. Second, in wye-connected, I can easily have ground-fault protection for the water pump. I can run an EGC to bond the motor metal casing with branch circuit enclosure and with the GEC at the main service disconnect. I don't think I have this liberty on delta high leg. As I see it, these three phase water pumps will be fed by an ungrounded delta source. Thus, I believe that an intricate and dedicated ground fault detection and isolation is recommended on each of these pumps.
Have you experienced the same situation? What did you do? Do you think it is better to stick with my drafted design (and purchase a separate small single phase step down transformer for single phase loads)? Or connecting to a high leg delta plus individual ground fault protection is worth it? What are your proposed ground fault protection and detection on this scenario?
I want to learn from your experiences. Consider me your youngest brother on this family and my question is solely out of curiosity and knowledge sharing. I don't intend to replace my current design without proper training.
Thank you for your time and knowledge.