Ground faults on the secondary of transformer as seen by the primary 3

Status
Not open for further replies.

gdeep

Electrical
Feb 9, 2012
17
Hi,

I have a 12.47kV/4.16kV 5MVA delta-wye(10A,10s resistive grounded system) feeding a 5kV switchgear. The NGR is rated for 10A, 10s and I am using SEL-751A protection relays.

1) A ground fault on the secondary of the transformer would be seen by the primary as L-L fault?
2) How would this 10A ground fault current be reflected on the primary? Would be there be a considerable increase in currents on two phases of the XFMR primary and would I be able to see negative sequence currents( I am using 800:5 CT)
3) Are there any good references I could use? I have tried simulating a model in PSCAD and I could see currents go up in two phases of the primary but I cannot verify the magnitude of the currents just the relative increase to the pre fault currents.

Any inputs would really be appreciated
Thanks
 
Replies continue below

Recommended for you

Thanks everyone! I guess, the mistake I made was using the formulas developed for normal balanced conditions during fault conditions. I can't simply multiply winding current by sqrt(3) to obtain line currents during fault conditions. Vector summation is needed here, which is what sibeen and LiteYear explained.
 