Electrical
- Nov 30, 2009
- 10
we are invoved in designing ground grid for a 63/20 Kv sub.(area: 120*80 sqm).The fence can not be included within ground grid area.the outer ground wire is 1 m inside the fence. our reccomendation is to isolate the fence from the grid and earth it seperatly but our client wants to connect the fence to the grid.
This induce a serious problem in design.we can not limit the touch voltage below tolorable voltage 1 meter outside the fence even with 2 m spaced ground rods along the grid perimeter.we would like to have your reccomendation on design and/or to justify the client for another design criteria.
I thank you in advance.
This induce a serious problem in design.we can not limit the touch voltage below tolorable voltage 1 meter outside the fence even with 2 m spaced ground rods along the grid perimeter.we would like to have your reccomendation on design and/or to justify the client for another design criteria.
I thank you in advance.