Hi all,
i'm working on the preliminary design for an outside substation ground grid. (underground incoming cables + 4 feeders and a capacitor bank). Metal-enclosed switchgear on a concrete slab.
I received the soil resistivity from the civil contractor and it is 3000 ohm-m !!
so I started playing with the number using IEEE 80-2000.
With an area of 2500 pi^2, and , 500 pi of buried conductor, I get a grid resistance of about 100 ohm!, which is way above the recommended 5 ohm. But it is almost impossible to go lower than that with a 3000 ohm-m soil resistivity.
The fault current is 2675A and L-N voltage is 14.4 kV.
What I understand is that with a grid resistance that high, almost 100% of the fault current will go back to the source through the shield of the incoming underground cables.
So my question is , what current do I use to calculate the step and mesh voltages (or what is the value of the split factor)...
Also, what happens with GPR? I know it cannot go higher than L-N voltage, but it will probably be way above the recommended 5000 V.
Thanks in advance for your comments and answers about ground grid design with very high soil resistivity.
JL
i'm working on the preliminary design for an outside substation ground grid. (underground incoming cables + 4 feeders and a capacitor bank). Metal-enclosed switchgear on a concrete slab.
I received the soil resistivity from the civil contractor and it is 3000 ohm-m !!
so I started playing with the number using IEEE 80-2000.
With an area of 2500 pi^2, and , 500 pi of buried conductor, I get a grid resistance of about 100 ohm!, which is way above the recommended 5 ohm. But it is almost impossible to go lower than that with a 3000 ohm-m soil resistivity.
The fault current is 2675A and L-N voltage is 14.4 kV.
What I understand is that with a grid resistance that high, almost 100% of the fault current will go back to the source through the shield of the incoming underground cables.
So my question is , what current do I use to calculate the step and mesh voltages (or what is the value of the split factor)...
Also, what happens with GPR? I know it cannot go higher than L-N voltage, but it will probably be way above the recommended 5000 V.
Thanks in advance for your comments and answers about ground grid design with very high soil resistivity.
JL