We recently had a costly incident in our mill that resulted in the destruction of 6 VFDs. These drives are in a section of the mill that is supplied by a transformer with a ungrounded 480 V delta secondary. It appears that the damage resulted from over voltages created by an intermittent arcing fault in an underground feeder.
In order to prevent future damage from similar incidents, I believe that we need to get the system grounded. My first inclination is to simply corner ground the transformer and monitor for ground current so that we know if the B phase gets grounded elsewhere. However, I am also considering using a Zig-zag transformer to create a neutral point.
Outside of the issue of resistance grounding, are there any advantages of the Zig-zag transformer over a corner grounded system? Are there any unforeseen problems that could result from corner grounding?
In order to prevent future damage from similar incidents, I believe that we need to get the system grounded. My first inclination is to simply corner ground the transformer and monitor for ground current so that we know if the B phase gets grounded elsewhere. However, I am also considering using a Zig-zag transformer to create a neutral point.