ThePunisher
Electrical
- Nov 7, 2009
- 384
HI all,
I have been designing several industrial substations in the past and I always design the substation grounding mesh grid per IEEE 80 and as a "stand-alone" grounding grid. This means, I do not consider any bonding to the overall plant grid and design to be inherently safe and not rely to plant grid bonding.
I was given a grounding report (35 kV level and 3 kA L-G fault, solidly grounded system)and the engineer was not able to meet 3000 V GPR and touch and step potentials with expanded substation grid. So he used and modeled the plant grid along in ETAP and of course got his Vstep and Vtouch within limits. However, I am not comfortable relying on plant grid for the safety of the substation. Is this acceptable to some extent or exception???
I was thinking using deep ground rod (40-60 meters) instead of relying on plant grid.
Appreciate all comments and suggestions.
I have been designing several industrial substations in the past and I always design the substation grounding mesh grid per IEEE 80 and as a "stand-alone" grounding grid. This means, I do not consider any bonding to the overall plant grid and design to be inherently safe and not rely to plant grid bonding.
I was given a grounding report (35 kV level and 3 kA L-G fault, solidly grounded system)and the engineer was not able to meet 3000 V GPR and touch and step potentials with expanded substation grid. So he used and modeled the plant grid along in ETAP and of course got his Vstep and Vtouch within limits. However, I am not comfortable relying on plant grid for the safety of the substation. Is this acceptable to some extent or exception???
I was thinking using deep ground rod (40-60 meters) instead of relying on plant grid.
Appreciate all comments and suggestions.