Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations The Obturator on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Grounding of Equipment

Status
Not open for further replies.

JGnewjersey

Electrical
Jun 10, 2016
2
See attached photo

The PT transformer is grounded to the steel. The 13kv cable shield is grounded to the steel.

I believe both should be connected to the copper ground grid connection at the base of the steel. Not to the steel and then to the copper ground grid.

Please help me with references that I can use in my claim, if I am correct.

Many Thanks
JGnewjersey
 
 http://files.engineering.com/getfile.aspx?folder=22cf4e07-df65-41e3-b515-de303540fb14&file=2PT_Ground_Step_up_yard.jpg
Replies continue below

Recommended for you

If the steel has a proper connection to the Grounding electrode system (see definition in Part III of Article 250(specifically2 250.52 (A) (2) of the NEC) then yes connecting to the steel is permitted.

If you have access to the NEC handbook that have nice illustrations that convey the above code references to assist you in understanding what is trying to be conveyed.

Exhibit 250.29 in the Handbook has a picture of a panel that connects to building steel which is connected to the ground ring.

A quick search returned some other discussions and info related to your inquiry.




So you are correct if the above code references are not met and your adversary would be correct if it does.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor