constantlylearning
Electrical
- Jan 5, 2006
- 38
I think it's a common rule that you usually want to install a surge arrester as close as possible to the terminals of the equipment you're trying to protect. One of the primary reasons is that increased lead length between the transformer terminals and the arrester terminals increases voltage drop along the leads and reduces the protective margins. So, having a very short grounding lead between the arrester base and a grounding pad on the tank wall decreases (as much as possible) the total voltage drop between the transformer tank (ground) and the transformer terminal during a lightning arrester discharge.
My question is:
In addition to the 1 to 2 foot copper lead between the arrester base and the tank wall, would it not also be advantageous to include a copper lead from the arrester base down to the ground grid pigtail. My reasoning is that the transformer tank wall is the ground reference for voltage transient protection, so you definitely want the arrester grounded directly to the tank wall. However, you might not want the tank wall to be your primary fault path for 60 Hz current during a lightning arrester failure. In truth, I don't know how the 60 Hz impedance for a 4/0 copper lead vs. a transformer tank compares. It could be that the tank is a lower imepdance path to 60 Hz current as well as fast transients like lightning and the 4/0 lead would conduct very little 60 Hz fault current. Does anyone know what the standard practice is? I did not find a reference to this in C62.22.
Please see the linked GIF file. The red down lead is the one in question.
My question is:
In addition to the 1 to 2 foot copper lead between the arrester base and the tank wall, would it not also be advantageous to include a copper lead from the arrester base down to the ground grid pigtail. My reasoning is that the transformer tank wall is the ground reference for voltage transient protection, so you definitely want the arrester grounded directly to the tank wall. However, you might not want the tank wall to be your primary fault path for 60 Hz current during a lightning arrester failure. In truth, I don't know how the 60 Hz impedance for a 4/0 copper lead vs. a transformer tank compares. It could be that the tank is a lower imepdance path to 60 Hz current as well as fast transients like lightning and the 4/0 lead would conduct very little 60 Hz fault current. Does anyone know what the standard practice is? I did not find a reference to this in C62.22.
Please see the linked GIF file. The red down lead is the one in question.