Grounding on Offshore Metallic structure 1

Status
Not open for further replies.

jay80

Electrical
Apr 6, 2013
7
0
0
AE
Hi,
On a fixed offshore oil & gas structure which is completely metallic, Is there any need for a common bonding network, if each equipment is bonded to the metallic structure by cad weld.
Thanks in advance.
Regards
Jay
 
Replies continue below

Recommended for you

Hi
According to IEC60079-14 §6.3 all exposed and extraneous conductive parts shall be connected to the equipotential bonding system which is normally the steel structure.
It is however not required to use seperate conductors if the parts are firmly secured and in conductive contact whith the equipotential bonding system which is the case with a welded connections.
Best Regards
Preben
 