- Dec 31, 2015
- 10
Hi,
If designing grounding for a new fabrication facility that is 500’W x 1000’L and that it is intended to have a perimeter ground grid, plus we plan on installing 10’L ground rods periodically, what's the appropriate spacing for those rods?
NEC 250.53 (B) requires a minimum of 6-ft between electrodes (for multiple rods situation), but no maximum spacing requirement. The article below suggests 2X of rod length (e.g., ~20 feet spacing for 10 feet L rod). However, it still results in way too many rods for an industrial facility in that size. Is it required to install them in this manner or is there any variance? Suggestions?
Thanks,
JS
If designing grounding for a new fabrication facility that is 500’W x 1000’L and that it is intended to have a perimeter ground grid, plus we plan on installing 10’L ground rods periodically, what's the appropriate spacing for those rods?
NEC 250.53 (B) requires a minimum of 6-ft between electrodes (for multiple rods situation), but no maximum spacing requirement. The article below suggests 2X of rod length (e.g., ~20 feet spacing for 10 feet L rod). However, it still results in way too many rods for an industrial facility in that size. Is it required to install them in this manner or is there any variance? Suggestions?