rockman7892
Electrical
- Apr 7, 2008
- 1,156
In relation to my other recent post I'm looking at an application where there are (3) 3MW wind turbines connected to a 12.47kV collector feeder before interconnecting to a 12.47kV distribution line (there is actually a voltage regular between turbines and utility line to bring 12kV turbine voltage up to 12.47kV.
The collector feeder is interconnected to the 12.47kV utility line through a re-closer and just prior to the recloser on the generation side there is a Delta-Wye grounding transformer. I'm trying to figure out the role of this grounding transformer. My assumption is that if there is a ground fault on collection feeder recloser will detect but once recloser opens the grounding transformer is there to provide a ground fault source to allow wind turbines to detect and shut down? Without this grounding transformer once the re-closer opens with no ground fault source the turbines may not be able to detect ground fault (assuming turbines have a wye-delta step up at each turbine with delta side facing collection feeder but trying to confirm).
Is my assumption above for purpose of grounding transformer correct? I've never seen one that operates in parallel to the utility (usually see grounding transformer on delta side of transformer).
The utility is now going to upgrade distribution line from 12.47kV to 24.9kV requiring us to put in a step-up transformer on collector feeder to step voltage up to 24.7kV. Planned location for this transformer is after re-closer existing (re-closer will remain as xfmr LV protection) and then a new 25kV rated recloser will be located on transformer HV side to connect it to utility line.
With the addition of this transformer, I'm trying to determine impact it will have on grounding transformer. Typically I'd see a Delta-Wye interconnection transformer with delta on LV collector side this in this case allowing grounding transformer to be sole source of ground fault current on collector system. I have seen however that the utility may require a wye-gnd / wye-gnd interconnection transformer and have seen a similar nearby site with a wye/wye interconnection transformer have the grounding transformer on the utility side of transformer.
Appreciate any feedback on the above as it relates to existing grounding transformer impact on delta/wye transformer as well as a potential wye/wye transformer.
Thanks