GUY INITIAL TENSION

Status
Not open for further replies.

LOKSTR

Structural
Apr 15, 2005
122
What is "Guy initial tension" and why is it important? Is there any reference material available online for its calculation?

Thanks
 
Replies continue below

Recommended for you

That would be the tension in the guy wire when it is installed. Depending on your application, it may not make much difference. However in some applications it could be critical. If the initial tension is high for a guyed tower and the temperature drops significantly, it could buckle the tower. That may be an extreme example, but hope you get the point. There is quite a bit of information out there, what is your application?
 
For guyed wood, concrete and steel transmission poles, we use a pretension of 2% of the ultimate guy tension. What program are you using to do the structural analysis?

_____________________________________
I have been called "A storehouse of worthless information" many times.
 
You will find allowable limits in TIA/EIA-222-F, Section 6 and Annex E regarding initial tension and plumb of towers.

Regards,
Lutfi
 