MechEng2007
Mechanical
- Apr 24, 2009
- 14
Hi - Thanks in advance for any help on this issue.
We have a 4" pipe feeding back-to-back attic sprinklers in an attic with standard 2x4 roof trusses; the pipe will be running perpendicular to the trusses. What is an acceptable method to hang this pipe per NFPA 13 (2022 edition)?
Option 1: Per 17.2.4.3 - Install 2.5" Wood Sammy's into the bottom (vertically) of the top chord 2x4 every 14 ft. Wood Sammy Model is GST 25-380 ( Is this acceptable and am I using the correct code reference?
Option 2: Per 17.2.4.3.2 - Install 2" Wood Sammy's into the side (horizontally) of the top chord 2x4 every 10 ft. Wood Sammy Model is SWG 20 ( Is this acceptable as well?
General Question: Does NFPA 13 ever permit the use of a Wood Sammy with a 1/4" screw size? I cannot see that they do.
The local AHJ is quizzing me about which section of NFPA 13 permits the hanging method I want to use.... I have a feeling he knows I am making a mistake which is very possible. Looking at the details and figures in the Sammy catalog and reading NFPA 13 has me second-guessing myself about which method, if any, is acceptable.
We have a 4" pipe feeding back-to-back attic sprinklers in an attic with standard 2x4 roof trusses; the pipe will be running perpendicular to the trusses. What is an acceptable method to hang this pipe per NFPA 13 (2022 edition)?
Option 1: Per 17.2.4.3 - Install 2.5" Wood Sammy's into the bottom (vertically) of the top chord 2x4 every 14 ft. Wood Sammy Model is GST 25-380 ( Is this acceptable and am I using the correct code reference?
Option 2: Per 17.2.4.3.2 - Install 2" Wood Sammy's into the side (horizontally) of the top chord 2x4 every 10 ft. Wood Sammy Model is SWG 20 ( Is this acceptable as well?
General Question: Does NFPA 13 ever permit the use of a Wood Sammy with a 1/4" screw size? I cannot see that they do.
The local AHJ is quizzing me about which section of NFPA 13 permits the hanging method I want to use.... I have a feeling he knows I am making a mistake which is very possible. Looking at the details and figures in the Sammy catalog and reading NFPA 13 has me second-guessing myself about which method, if any, is acceptable.