HI
i am using a 100% FA A.H.U. with a cap. of 2000 L/S with heat recovery this AHU IS DX PACKAGE UNIT HAP output data was that the total coil load = the sensible load and it cannot be right ! there is for sure a latent load cause when i changed the type of the AHU to tempering it calculates the latent load on the coil .can i took the loads "total and sensible" only from the hap as the type " chilled water coil tempering “regardless of the actually used type DX COIL i mean??
at air system properties iam using air terminal units –split dx fan coil units the ventilation option is either
1-common ventilation system
2- direct ventilation system
the Fresh air must be supplied in 23C so after the cooling and dehumidification FA needs reheat how can i control all this on hap?
If I have the 100 % FA then I ll chose the common ventilation system and from it I ll chose vent system component what I need to be sure is if the cooling coil set point and vent reclaim tabs are the description of the 100% FA equipment I am using to serve these zones ?
Thanks in advance
i am using a 100% FA A.H.U. with a cap. of 2000 L/S with heat recovery this AHU IS DX PACKAGE UNIT HAP output data was that the total coil load = the sensible load and it cannot be right ! there is for sure a latent load cause when i changed the type of the AHU to tempering it calculates the latent load on the coil .can i took the loads "total and sensible" only from the hap as the type " chilled water coil tempering “regardless of the actually used type DX COIL i mean??
at air system properties iam using air terminal units –split dx fan coil units the ventilation option is either
1-common ventilation system
2- direct ventilation system
the Fresh air must be supplied in 23C so after the cooling and dehumidification FA needs reheat how can i control all this on hap?
If I have the 100 % FA then I ll chose the common ventilation system and from it I ll chose vent system component what I need to be sure is if the cooling coil set point and vent reclaim tabs are the description of the 100% FA equipment I am using to serve these zones ?