We are building a wastewater plant in regional Victoria Australia and I have a problem with harmonics mitigation. System particulars:
22KV Utility with 3050A available short circuit current.
One 22KV switchboard distributing power to four 2500KVA transformers.
Two 4000A main-tie-main switchboards(MSB1 and MSB2)distributing 415V Three phase 50HZ to six motor control centers.
MSB1 feeds four MCC's: Two are in the same room as MSB1 each with 500KVA VFD load and 300KVA linear load. Two other MCC's are 100m away each with 400KVA VFD load and 200KVA linear load
MSB2 feeds two MCC's both in the same room each with 1000KVA VFD load and 200KVA linear load.
Yes it is a harmonic rich environment.
Our specification states 3% THD at PCC and 5% THD at each MCC bus. We have specified 6 pulse VFD's with DC chokes.
My question is it better to install active filtration at each MCC bus or can we correct at the MSB level? My VFD vendor claims it will work better at the MSB level, but I am concerned about the harmonic currents within the MCC's.
Cheers!
22KV Utility with 3050A available short circuit current.
One 22KV switchboard distributing power to four 2500KVA transformers.
Two 4000A main-tie-main switchboards(MSB1 and MSB2)distributing 415V Three phase 50HZ to six motor control centers.
MSB1 feeds four MCC's: Two are in the same room as MSB1 each with 500KVA VFD load and 300KVA linear load. Two other MCC's are 100m away each with 400KVA VFD load and 200KVA linear load
MSB2 feeds two MCC's both in the same room each with 1000KVA VFD load and 200KVA linear load.
Yes it is a harmonic rich environment.
Our specification states 3% THD at PCC and 5% THD at each MCC bus. We have specified 6 pulse VFD's with DC chokes.
My question is it better to install active filtration at each MCC bus or can we correct at the MSB level? My VFD vendor claims it will work better at the MSB level, but I am concerned about the harmonic currents within the MCC's.
Cheers!