Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Harmonic reduction using transformer primary connections

Status
Not open for further replies.

norske

Electrical
Jun 18, 2003
13
Hi everyone,

We use three transformers (2MVA, 11kV/500V) to each supply different DC drives. The vector groups are Dyn1, Dyn11, and Dz0. The transformers are feed from the same CB this being the "point of common coupling"

I believe the different vector groups are used to smooth out any harmonics that appear at the point of common coupling on the HV side. Can anyone tell me how effective this method is? Also how do I calculate the level of harmonic distortion at the HV terminals for ea of these vector groups?

Many thanks to all in advance.
 
Replies continue below

Recommended for you

This is commonly done for multiple rectifier units in smelting facilities and the like.

It's very effective at reducing total harmonic distortion seen on the primary.

I don't have a good reference on how to quantitatively calculate the harmonic reduction, but I'm sure someone will.

 

Search this site for 6-, 12-, 18- and 24-pulse rectification.

IEEE Std 519-1992 may have applicable information.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor