I'm designing a system with a standby generator (~150kW), where most of the load will be 6 pulse VFD's. The generator will be sized to account for the additional heating in the alternator due to the harmonic currents.
My question is, what is an acceptable limit for harmonic voltage distortion. 5% THD seems to be a common limit for utilities, but this will be difficult to achieve on the generator. Is a higher level of THD acceptable for the relatively short periods when the standby generator will be running? Are there any relavent standards? I could install harmonic filters on all of the drives but I have heard of compatibility issues with gensets.
The loads are primarily VFD's, lighting, heating, and a PLC-based control system.
My question is, what is an acceptable limit for harmonic voltage distortion. 5% THD seems to be a common limit for utilities, but this will be difficult to achieve on the generator. Is a higher level of THD acceptable for the relatively short periods when the standby generator will be running? Are there any relavent standards? I could install harmonic filters on all of the drives but I have heard of compatibility issues with gensets.