Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

HART-only device connected to HART AI channel

Status
Not open for further replies.

123MB

Electrical
Apr 25, 2008
265
Has anyone ever connected a HART-only device (i.e. without 4-20mA) onto a HART AI module?
 
Replies continue below

Recommended for you

No. It's not a functional concept.

The FSK modulated HART signal is superimposed on the current signal.

HART infers a current signal as well. For point-to-point, it's a 4-20mA signal. For multidrop, it's 4mA fixed. But there's always a current signal.
 
Why not just make a dummy current loop using fixed resistors then add the FSK Hart signal in series. The total loop resistance could be about 2k with the HART imposed over a fraction of that. You might have to experiment a little, perhaps some small capacitors to couple the signal across the resistance.
 