Population Density 37 p/ha
Peeking Factor
Ave. Consumption 600 L/d per person
Min. Rate 0.4
Max. Day 2.75
Peak Rate 4.13
Fire Flow 75.8 L/s
Max. Dist for Hydrants 150 m
Area (ha) 14.54
Population Density (persons/ha) 37
Total Population (persons) 538.0
Ave. Consumption (L/s per person) 3.73597
Min.Ave. Demand ( L/sec) 3.74
i need these values :
Min. Daily Demand (L/sec)
Max. Daily Demand (L/sec)
Max. Day Demand + Fire Flow (L/sec)
Max. Hourly Demand (L/sec)
Google Ten States Standards. It should have the information you need.
There are also US government Unified Facilities Criteria (UFC), some of which are old technical manuals.
These will have the procedures you can follow if there are no local standards.
Ave. Consumption 600 L/d per person * Total Population (persons) 538.0 * Min. Rate 0.4 /86400 = Min. Daily Demand (L/sec)
Ave. Consumption 600 L/d per person * Total Population (persons) 538.0 * Max. Day 2.75 /86400 = Max. Daily Demand (L/sec)
(Ave. Consumption 600 L/d per person * Total Population (persons) 538.0 * Max. Day 2.75 /86400) + (Fire Flow 75.8 L/s Max. Daily Demand (L/sec)) = Max. Day Demand + Fire Flow (L/sec)
Ave. Consumption 600 L/d per person * Total Population (persons) 538.0 *Peak Rate 4.13 /86400 = Max. Hourly Demand (L/sec)