I'm currently working on a wastewater construction project. In our design we have asked for a flared inlet, from 48" to 42", for the suction line connection to the wet well. The contractor has submitted a concentric reducer to replace the flared inlet. Is there a significant head loss when comparing the two different inlets?
I have found that the K(flare) = .04 best case
I have found that the K(conc.) = .5 worst case if the entrance was a straight edge and not at an angle.
Do you think these values are accurate or can anyone come up with a better K(conc) value?
I have found that the K(flare) = .04 best case
I have found that the K(conc.) = .5 worst case if the entrance was a straight edge and not at an angle.
Do you think these values are accurate or can anyone come up with a better K(conc) value?