MinnesotaSlinger
Mechanical
- Feb 13, 2008
- 23
Suppose you're calculating head loss within a piping system for radiative or reheat piping, for which the water flowing through it will be 150-180 F. When you refer to a flow of 1 gpm, does that generally mean 1 gallon (i.e., 0.1337 cubic feet) of volume at 150-180 F or does it mean 1 gallon at standard conditions (like 60 F) that would actually take up more than 0.1337 cubic feet at the higher temperature. Because of the expansion of water, 1 cubic foot of water at 60 F will take up about 1.025 cubic feet at 165 F. So, 1 gpm at 60 F will have to flow 2.5% faster at 165 F. Given that head loss is roughly proportional to velocity squared (it is except for the change in friction factor, which would be small in this case), that means that head loss would be 5% more. That's not a huge difference, but it does seem significant enough to consider for proper pump selection.
So basically, when referring to a flow of x gpm, are those gallons standardized to, say, 60 F or is a gallon the amount of water that occupies 0.1337 cubic feet at whatever temperature it's at?
Thanks.
So basically, when referring to a flow of x gpm, are those gallons standardized to, say, 60 F or is a gallon the amount of water that occupies 0.1337 cubic feet at whatever temperature it's at?
Thanks.