waynegu
Electrical
- May 20, 2012
- 4
Hi,
I am working on a 33kV cable project and using the heat shrink joint kits for the In-Line Joints.
I meggered the cable before jointing every time and the 5kV DC IR (core - sheath) reading was always around 400GOMHS/1min, and I also meggered the cable with the new In-Line joint after 3 days, and the IR reading varied, 5 of 10 were 300GOHMS/1min, 3 of 10 were close to 100GOHMS/1min, and the other 2 were less than 20GOHMS/1min.
I decided to strip one low IR reading joint open to analyse the cause of the problem. Finally, I found out one heat shrink tubing was only 20GOHMS/1min, however, before heating it was 500GOHMS/1min. I also checked the tubing and found there was no obvious over heating signs on it.
Have anyone had the same experience before? Will this tubing cause the cable failure during normal operation?
Thanks for the help in advance.
Wayne
I am working on a 33kV cable project and using the heat shrink joint kits for the In-Line Joints.
I meggered the cable before jointing every time and the 5kV DC IR (core - sheath) reading was always around 400GOMHS/1min, and I also meggered the cable with the new In-Line joint after 3 days, and the IR reading varied, 5 of 10 were 300GOHMS/1min, 3 of 10 were close to 100GOHMS/1min, and the other 2 were less than 20GOHMS/1min.
I decided to strip one low IR reading joint open to analyse the cause of the problem. Finally, I found out one heat shrink tubing was only 20GOHMS/1min, however, before heating it was 500GOHMS/1min. I also checked the tubing and found there was no obvious over heating signs on it.
Have anyone had the same experience before? Will this tubing cause the cable failure during normal operation?
Thanks for the help in advance.
Wayne