GBor
Mechanical
- Feb 1, 2005
- 1,497
A bit out of my league here. I have 3 electronics boxes being installed on a rack. They exhaust heat into a plenum which has a pull-through cooling system. I have the fan characteristics with CFM to static pressure. Plenum is a little deeper than 3", and we are looking to attach a 3" diameter duct. Required airflow for the three boxes is 27 CFM at 40C, 27 CFM at 40C, and 20 CFM at 55C. Static pressure drops max are 0.07 inH2O, 0.06 inH2O, and 0.13 inH2O, respectively. The boxes are each sitting on a 4MCU short-short Airinc tray and completely cover the top of the plenum. Friction due to bends will be minimal (probably negligible).
When I start to think about the restrictions caused by knocking out the plugs in the bottom of the Airinc trays, I get turned around in the analysis. Fluids book isn't helping me here...been too long and cobwebs are really strong!
Any guidance on how to balance the airflow?
When I start to think about the restrictions caused by knocking out the plugs in the bottom of the Airinc trays, I get turned around in the analysis. Fluids book isn't helping me here...been too long and cobwebs are really strong!
Any guidance on how to balance the airflow?