We are currently putting a package together with a compressor and a gen set and want to cool both units on one cooling circuit. I'm a rusty with thermo so I thought I would turn here. Here are the specs.
Total heat load will be 150,000 BTU/hr
Ambiant temp is 100 F.
We want the coolant out around 120 F.
Using a 60/40 solution of Eth. Gly. and H2O specific heat is around 0.75.
We were thinking of a flow rate of 10 GPM but that along with the size is still TBD.
We would like to find out the temperature of the coolant going into the exchanger. Possibly a way to figure out the unknowns as well. Thanks!