Heat Flow in a Pipe with integrated Sensor
Hanzo1987
Aerospace
Oct 27, 2020
19
I have the following problem and hope you can help me. I have the setup as shown in the drawing. A pipe that is flowed through, and in the middle of it another pipe, but at the end of this branch is a sensor. Initially the fluid would flow, with a temperature of 25°C. If my thought is correct, the pipe with the sensor (if there is a drain valve) would fill with the liquid and then rest, because there would be no more flow, since it has nowhere to flow.
Now the liquid is slowly heated (heating to about 350°C) and continues to flow the same way. How would the temperature in the branch change? This would have to be still relatively cold at the sensor, since no exchange of the liquid takes place, since no flow is present in the branch, or do I have there a mistake in my thought?
How would you calculate the heat exchange between the flowing and standing medium? Because there is heat exchange only there, which would then have to be "up" through the entire water column. Can we calculate this in a simplified way as forced convection on a plane wall and assume the fluid portion in the branch as a plane wall?
I hope the problem is apparent, because I would need to calculate the length of the branch so that a certain temperature at the sensor is not exceeded.
Thanks a lot!
 https://files.engineering.com/getfile.aspx?folder=43355935-b9ca-447a-884a-92f9ef95db7c&file=Rohr.png
Yes tahts right. But to simplify it I wantet to calculate it with the thermal restistance of the resting oil in the capillary and ignore the convection. Or is my thought to simplified?
Your thoughts are way too simplified, and there is little you can calculate to come even close to an accurate answer. Hot fluids rise causing natural convection, which will help to transfer heat upwards but hinder heat transfer downwards. A simple check valve at the tee location can stop much of this.
Okay, I think ig got your point. Do you think it is better (and easier) to simulate the heat transfer using ANSYS instead of calculating it manually?
Free convection coefficient for water is on the order of 10 times that of air, so it's likely that the sensor temperature will be closer to the free stream temperature than not.
TTFN (ta ta for now)