Heat gain from Lighting

Status
Not open for further replies.

Deweyirl

Mechanical
Jun 5, 2019
1
Hi all,

If in a room, a lighting design was carried out and the room will contain 4 no, LED luminaries with a total wattage of 80.

My query relates to what would a reasonable figure or percentage be to use as heat gain from the light. Of the 80 watts, how much of it would go into heat?

I am unable to find it in either a CIBSE guide or an Ashrea guide.

Your help would be gratefully welcomed.
 
Replies continue below

Recommended for you

Note that depending on the type of fixture (i.e. recesssed), a percentage of that can go into the plenum. This will be a coil load, but not a space load.
with today's LED and lower lighting wattage, probably not as important as in the old HID/fluorescent days.

In Trane Trace and other software you have a setting for the type of lighting and how it relates to space vs. plenum.
 