how is heat load of a machine is computed?this is to design the ventilation of a cleanroom..what is the formula in computing air balance?thanks...
 
Replies continue below

Recommended for you

The formula is Q = m.Cp.(Tout - Tin). You get Q from the manufacturer, or motor nameplates, or fuel consumption...

If you are exhausting from a room with tempered outdoor air makeup, then the Tin is your tempered air, and the Tout is the maximum temperature you want in the space. Cp = 1.005 kJ/kg and m/1.2 = Volume flow you require.

 