Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Heat Loss from a Closed Tank

Status
Not open for further replies.

BatesEngineer

Chemical
Sep 24, 2020
4
I have a large fire protection tank, 34ft tall x 29ft dia, holds 175000 gallons of water. I have a Lowest One Day Mean Temp of 25F and the min target temp is 42F. Tank is made of carbon steel.

Using the NFPA 22 figure 16.1.4, heat loss = square area x (heat difference) / R, I get a heat loss of 8,164kW, or 24 million BTU/hr.
Assumed: R=0.0031 ft2 F hr/BTU, A=4400 ft2, deltaT = 17

However using Q=hA(deltaT), I get a heat transfer rate of 12.4kW or 42308 BTU/hr
Assumed: h = 3.231 W/m2 K, deltaT = 9.44 K, A = 408m2

These are wildly different results and I can not seem to find the reason.

Thanks in advanced.
 
Replies continue below

Recommended for you

If I use h = 1/R, and convert your h = 3.231 W/m2 K. I get R = 1.757 ft2 F hr/BTU.

4400 x 17 / 1.757 = 42,562 BTU/hr.

Conversion error?

Good Luck,
Latexman
 
Ever just stared at something for the longest time and couldn't see it... Thanks Latexman!
 
Your h is a bit low, since it only accounts for ideal natural convection. somewhere between 5 and 7 W/m^2-K accounts for some wind and some radiation.

Your R, inverted, comes out to 1831.6979 W/m^2-K, so a factor of ~600 larger than your h; this magnitude is more for convection in a water-cooled application.

TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! faq731-376 forum1529 Entire Forum list
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor