Is this the correct way to calculate the ideal and real COP of the evaporator (Beta) and max efficiency of a table top ice maker using the heat transfer method???
Description: 110V ac compression refrigeration ice machine using refrigerant 134a.
An electronic controller with display controls the machine. An 110V ac electric motor runs a fan cooling the motor/compressor and condenser. The machine is plugged into a Watt meter which is plugged into an 110V ac receptacle.
1. 3 L of room temp tap water fills a reservoir
2. 500 mL of water is pumped from the reservoir into a tray containing the evaporator
3. 140 g of ice forms on the evaporator
4. The ice is scraped off into a second tray
5. Time it takes to form the ice is 600 s
6. The remainder of the water is returned to the reservoir
7. This cycle continues until the reservoir is empty.
8. Heat of fusion of ice = 333 kJ/kg
9. Cp of water = 4 kJ/kg K
10. Watt meter 190 W
11. Temp of condenser is 50 C
12. Temp of evaporator is -5 C
Solution for COP real = mass of ice X (heat of fusion of ice + Cp of water X (Temp of water in – temp water freeze)) / Work from a watt meter in Watts X time it takes to form the ice
Here are my concerns about this method.
1. The controller is responsible for 1 – 2 Watts and the fan motor 20ish Watts. This is not work done on the R-134a and should be subtracted from the Watt meter
2. The fact that there is a fan and you can’t comfortably keep your hand on the motor/compressor tells me that it’s not 100% efficient. Losses, ohmic, inductive, frictional. So an assumption has to be made about W to balance Qin+W-Qout=0
3. 500g of 21 C water is brought to the brink of freezing. Why count only the solid?
4. The above statement implies that including the heat of fusion of ice in the calculation is as relevant as the number of cars in the parking lot
5. The above statement, if true, implies that the time to make the ice is also irrelevant
6. Qout must also be calculated to balance the equation in statement 2
Typical COP for a compression refrigeration cycle is 2 to 6 Qin to Qout respectively.
Efficiency is on the order of 30 – 40 %
Description: 110V ac compression refrigeration ice machine using refrigerant 134a.
An electronic controller with display controls the machine. An 110V ac electric motor runs a fan cooling the motor/compressor and condenser. The machine is plugged into a Watt meter which is plugged into an 110V ac receptacle.
1. 3 L of room temp tap water fills a reservoir
2. 500 mL of water is pumped from the reservoir into a tray containing the evaporator
3. 140 g of ice forms on the evaporator
4. The ice is scraped off into a second tray
5. Time it takes to form the ice is 600 s
6. The remainder of the water is returned to the reservoir
7. This cycle continues until the reservoir is empty.
8. Heat of fusion of ice = 333 kJ/kg
9. Cp of water = 4 kJ/kg K
10. Watt meter 190 W
11. Temp of condenser is 50 C
12. Temp of evaporator is -5 C
Solution for COP real = mass of ice X (heat of fusion of ice + Cp of water X (Temp of water in – temp water freeze)) / Work from a watt meter in Watts X time it takes to form the ice
Here are my concerns about this method.
1. The controller is responsible for 1 – 2 Watts and the fan motor 20ish Watts. This is not work done on the R-134a and should be subtracted from the Watt meter
2. The fact that there is a fan and you can’t comfortably keep your hand on the motor/compressor tells me that it’s not 100% efficient. Losses, ohmic, inductive, frictional. So an assumption has to be made about W to balance Qin+W-Qout=0
3. 500g of 21 C water is brought to the brink of freezing. Why count only the solid?
4. The above statement implies that including the heat of fusion of ice in the calculation is as relevant as the number of cars in the parking lot
5. The above statement, if true, implies that the time to make the ice is also irrelevant
6. Qout must also be calculated to balance the equation in statement 2
Typical COP for a compression refrigeration cycle is 2 to 6 Qin to Qout respectively.
Efficiency is on the order of 30 – 40 %