jandlo
Structural
- Feb 28, 2006
- 31
I am working on a 5 over 1 mixed-use building with a composite steel podium. the 5 stories above are CFMF. The bearing walls align with the column lines. The resulting gravity loads are very large and the beams are quite big: up to W40x211. The upper floor diaphragms span laterally to the CMU stair towers, but the podium level has moment frame for the lateral support of only the podium level. So the lateral forces in the moment frames are not large. However, because we can't use flexible moment connections, the moment contribution from the gravity load is huge: Moments of up to 1,500 k-ft (factored LRFD).
Is this a common theme with this type of podium construction? I feel like these moment connections are going to be significantly over-designed. Thoughts?
Is this a common theme with this type of podium construction? I feel like these moment connections are going to be significantly over-designed. Thoughts?