vjr0512
Mechanical
- Jun 6, 2011
- 114
In one of the Heli Fuel package for the Northsea project, the filter water separator ( complying to API 1581) vessel bottom boot where the water is getting collected require any heat tracing ? (when the atm temperature is sub-zero) ? Client asks us to check for this scenario for such intermittent operation of the package . Vendor informs that this is not envisaged and recommends to drain the water after every fuel filling to ensure that the water does not stagnant there and hence no heat tracing is required.
The minimum atm temperature is -7 Deg C
Thanks to clarify
The minimum atm temperature is -7 Deg C
Thanks to clarify