Hello,
First time posting, looking forward to some insight. I am working on a deep foundation plan for a 2-story residential structure located near a waterbody (approximately 200 ft+ inland). I am utilizing a grade beam, helical pier system due to a relatively thick and soft organic soils layer 5' below existing grade (layer of organics is about 12' thick with N-Values of 2 or less).
Part of the foundation wall is 9 FT in height (retaining 8'-7" of soil). I am designing a triple helix square shaft tie-back to provide stability against the soil pressure (lateral restraint near top of wall), and utilizing a double helix 3.5" dia. helical at the footing to take up the vertical loads, with a 5" reinforced slab at the bottom of the wall providing sliding resistance. The helical tie-backs will likely be installed using a PVC sleeve in the wall, with a backer plate on the interior side of the reinforced concrete foundation wall as a connection. The reason for the tie-back is to prevent creating a typical cantilevered retaining wall (very expensive in my analysis, and not very safe/effective with soft soil) and to mitigate potential movement at the top of the wall that would then push against the wood floor framing.
My question is: Is there a feasible way to prevent water infiltration through the PVC sleeves? I am thinking of a sort of neoprene gasket to mount the plate over and tighten the threaded portion of the helical to create a seal. Yet, the area around the shaft itself is still an infiltration point. I have also considered using epoxy around the shaft in the PVC.
I have already considered embedding the plate in the wall, but I have calculated a 9.5 kip factored shear load on the 12" thick concrete wall, and my analysis on the shear with 8" embedment & steel reinforcement is unsatisfactory. Any recommendations or comments would be much appreciated, or if more information is required.
First time posting, looking forward to some insight. I am working on a deep foundation plan for a 2-story residential structure located near a waterbody (approximately 200 ft+ inland). I am utilizing a grade beam, helical pier system due to a relatively thick and soft organic soils layer 5' below existing grade (layer of organics is about 12' thick with N-Values of 2 or less).
Part of the foundation wall is 9 FT in height (retaining 8'-7" of soil). I am designing a triple helix square shaft tie-back to provide stability against the soil pressure (lateral restraint near top of wall), and utilizing a double helix 3.5" dia. helical at the footing to take up the vertical loads, with a 5" reinforced slab at the bottom of the wall providing sliding resistance. The helical tie-backs will likely be installed using a PVC sleeve in the wall, with a backer plate on the interior side of the reinforced concrete foundation wall as a connection. The reason for the tie-back is to prevent creating a typical cantilevered retaining wall (very expensive in my analysis, and not very safe/effective with soft soil) and to mitigate potential movement at the top of the wall that would then push against the wood floor framing.
My question is: Is there a feasible way to prevent water infiltration through the PVC sleeves? I am thinking of a sort of neoprene gasket to mount the plate over and tighten the threaded portion of the helical to create a seal. Yet, the area around the shaft itself is still an infiltration point. I have also considered using epoxy around the shaft in the PVC.
I have already considered embedding the plate in the wall, but I have calculated a 9.5 kip factored shear load on the 12" thick concrete wall, and my analysis on the shear with 8" embedment & steel reinforcement is unsatisfactory. Any recommendations or comments would be much appreciated, or if more information is required.