Asisraja D
Mechanical
- Jan 3, 2024
- 149
Hello professionals
we have planned to install fire hydrant system for our new plant and it contains 400KL static water tank and the pipelines layout i have shared here. i have calculated head loss for the entire piping system and i get large amount of pressure drop. i have attached my calculation sheet. i give you my calculation details below please review and explain me little bit in this.
Pipe diameter for main line = 150mm
Length of 150mm pipe is = 535.9 meters.
pipe diameter for branch connection = 100mm
Length of 100mm pipe is = 212.2 meters.
Static tank 400KL height is = 6.3 meters.
MOC of pipe is Mild steel so i took 0.045 as pipe roughness.
overall head loss is 5.71 bar. so (7-5.71 = 1.29 bar line pressure) This is very low pressure as per standards because we should maintain line pressure of 3 bar minimum.
Pump capacity as per standards = 2280 lpm , so pump capacity is 137 m3/hr. head is 70 meters as per vendor quotation.
Industry type : Fermentation & Chemical (API) Solvents used (chloroform, acetone,toluene)
As per IS 3844:1989 (Indian standards) industrial buildings above 15 meters but not exceeding 24 meters can have pump capacity of 2280 liters per minute of flow rate and pressure should be 3 kg/cm2 at fire hydrant line but we have faced huge head loss here. Does anyone help me if this much of head loss occurs then how can i achieve the required flow rate ? can i go for higher head for achieving this flow rate ? or else any other suggestions ?
i hope i can get your suggestions in this. Thank you all.
we have planned to install fire hydrant system for our new plant and it contains 400KL static water tank and the pipelines layout i have shared here. i have calculated head loss for the entire piping system and i get large amount of pressure drop. i have attached my calculation sheet. i give you my calculation details below please review and explain me little bit in this.
Pipe diameter for main line = 150mm
Length of 150mm pipe is = 535.9 meters.
pipe diameter for branch connection = 100mm
Length of 100mm pipe is = 212.2 meters.
Static tank 400KL height is = 6.3 meters.
MOC of pipe is Mild steel so i took 0.045 as pipe roughness.
overall head loss is 5.71 bar. so (7-5.71 = 1.29 bar line pressure) This is very low pressure as per standards because we should maintain line pressure of 3 bar minimum.
Pump capacity as per standards = 2280 lpm , so pump capacity is 137 m3/hr. head is 70 meters as per vendor quotation.
Industry type : Fermentation & Chemical (API) Solvents used (chloroform, acetone,toluene)
As per IS 3844:1989 (Indian standards) industrial buildings above 15 meters but not exceeding 24 meters can have pump capacity of 2280 liters per minute of flow rate and pressure should be 3 kg/cm2 at fire hydrant line but we have faced huge head loss here. Does anyone help me if this much of head loss occurs then how can i achieve the required flow rate ? can i go for higher head for achieving this flow rate ? or else any other suggestions ?
i hope i can get your suggestions in this. Thank you all.