thien2002
Mechanical
- Aug 13, 2002
- 110
I have a warehouse building in this space:
L= 108.75 FT
W= 80 FT
H Wall= 19 FT
H Susp. Roof = 10 FT
Area Floor= 8700SFT
Vol. Fan Level= 165300 CFT
Vol. Susp. Roof= 43500 CFT
Space below 14' Temp. = 55-65F
Space Above 14' Temp. = 65-71F
Differential Temp. = 10F
Hot Water Supply = 160F
Hot Water Return = 150F
Boiler = 160F
We are losing Heat from floor to 14'. Our Return Air Louver is at on top at 22'H and our Supply Duct is at approx. 20'H. Apparently there is a short circulation due to stratification and shorter cycle. There are several options:
A) Lower the Return Air Louver to about 3'H above floor, and increase Boiler Capacity since Boiler only operates at 160F while Design indicates 180F.
B) Purchase 2 new Fans at 16' blades @ cost = $4000 ea. from Big Ass Fans to de-stratify.
C) Rearrange Air Distribution by lowering diffusers to about 3-5' and lower the Return Air Louver to about 3'H above floor.
I think option A) is the best but I don't know if Energy cost to crank boiler up to 20F would be the energy cost issues. Please consult. Thank you!
L= 108.75 FT
W= 80 FT
H Wall= 19 FT
H Susp. Roof = 10 FT
Area Floor= 8700SFT
Vol. Fan Level= 165300 CFT
Vol. Susp. Roof= 43500 CFT
Space below 14' Temp. = 55-65F
Space Above 14' Temp. = 65-71F
Differential Temp. = 10F
Hot Water Supply = 160F
Hot Water Return = 150F
Boiler = 160F
We are losing Heat from floor to 14'. Our Return Air Louver is at on top at 22'H and our Supply Duct is at approx. 20'H. Apparently there is a short circulation due to stratification and shorter cycle. There are several options:
A) Lower the Return Air Louver to about 3'H above floor, and increase Boiler Capacity since Boiler only operates at 160F while Design indicates 180F.
B) Purchase 2 new Fans at 16' blades @ cost = $4000 ea. from Big Ass Fans to de-stratify.
C) Rearrange Air Distribution by lowering diffusers to about 3-5' and lower the Return Air Louver to about 3'H above floor.
I think option A) is the best but I don't know if Energy cost to crank boiler up to 20F would be the energy cost issues. Please consult. Thank you!