bigheadted
Electrical
- Jul 22, 2005
- 53
The main transformer that feeds our plant is a 100kva transformer that feeds a 1600kva breaker at 433v
how can i work out the maximum line current that i can pull on each phase before triping the breaker?
IL=(KVA.1000)/(VL.1.73)= 2135A per phase is this correct?
is it also true to say that if i have witnessed the plant running at full load of with a 0.98 pf p1=1659A
p2=1635A and P3 =1626A then i can use the figures as a rough guide to how much energy the press requires to turn at unity power factor and then calculate the affects of a lower power factor
KW= (IL.VL.1.73.PF)/(1000) taking the highest line current 1659A pf0.98 = 1218kw
Now if the power factor drops to 0.8
IL=(KW.1000)/VL.1.73.0.8= 2032A
am i along the right lines here because if i am thats very close to the breaker rating
The power factor correction we use consists of 15 banks of 46kvar delta connected three phase capacitors.
After checking it recently we found the yellow phase fuses blown on 12 of the 15 banks.
on the next production we lost the main breaker
How can i calculate the affects this would have had using the above data? could someone plese help me with the more complicated formulas
so that i can work it out for myself
how can i work out the maximum line current that i can pull on each phase before triping the breaker?
IL=(KVA.1000)/(VL.1.73)= 2135A per phase is this correct?
is it also true to say that if i have witnessed the plant running at full load of with a 0.98 pf p1=1659A
p2=1635A and P3 =1626A then i can use the figures as a rough guide to how much energy the press requires to turn at unity power factor and then calculate the affects of a lower power factor
KW= (IL.VL.1.73.PF)/(1000) taking the highest line current 1659A pf0.98 = 1218kw
Now if the power factor drops to 0.8
IL=(KW.1000)/VL.1.73.0.8= 2032A
am i along the right lines here because if i am thats very close to the breaker rating
The power factor correction we use consists of 15 banks of 46kvar delta connected three phase capacitors.
After checking it recently we found the yellow phase fuses blown on 12 of the 15 banks.
on the next production we lost the main breaker
How can i calculate the affects this would have had using the above data? could someone plese help me with the more complicated formulas
so that i can work it out for myself