Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Hi How to determine the return a 2

Status
Not open for further replies.

flamearrow

Mechanical
Jan 13, 2016
29
0
0
LK
Hi

How to determine the return air flow rate and exhaust air flow rate of AHU? OA & supply air shall be calculated. all I know return has to be same as supply and OA shall be subtracted, but I found in other designs that return is taken 2-10% less the the supply rate ,can anyone please tell explain Why?
 
Replies continue below

Recommended for you

There's no situation where your return air + outdoor air won't equal your supply air, that's simple conservation of mass. I haven't seen it but maybe some designs account for some sort of leakage or changes in air density?
 
As IRstuff said, the numbers add up. You also have to remove the exhaust airflow from the supply: RA - EA + OA = SA

The air that isn't returned will leave the room through openings to other spaces and as exfiltration.
 
Thanks Gents,

I would like to know the EA and RA rates, I mean I the designer came up with those numbers?
is there any rules to size the return flow or is it from the equipment data?

 
Your drawing says it there:
It will be controlled by the CO2 sensor.
If you have an increase on occupancy, your CO2 will rise and it will trigger the opening of the motorized damper to exhaust the air (you don't want to recirculate air with excessive CO2).
At the same time, to compensate your additional extracted air your motorized damper in the fresh air side will open as well.
Not sure exactly what is your doubt.
 
Miko123 said:
I would like to know the EA and RA rates, I mean I the designer came up with those numbers?
is there any rules to size the return flow or is it from the equipment data?

The designer is allowing a 11% of the air that is supplied into the Cafeteria to leak out (and/or to be exhausted), avoiding infiltration of non-conditioned air through exterior doors and/or windows and/or elevator doors.

He could follow a general requirement of keeping the space 10% pressurized or he could calculate how much air actually leaks out (and/or is exhausted), using an estimate volume of air per door or window.

Physically, he is using the blower of the roof package unit to achieve that slight pressurization of the Cafeteria.
The extreme of this situation would be a 100% fresh air unit with zero return: all OA is forced to leak out and/or it is removed by exhaust fans.

"Where the spirit does not work with the hand, there is no art." - Leonardo da Vinci
 
Thank you all for the replies,


Lnewqban, yes the infiltration should have been taken into account. either +/- pressure, we can calculate certain amount of air to compensate.
could you please help me to calculate the infiltration rate?
 
Infiltration happens due to wind pressure and stack effect (for tall buildings).
Buildings should blow, not suck, keeping humid hot air out.
Exhaust and leakage flow rates should be less than intake (OA) in order to maintain positive pressure (except for kitchens).

Take a look at this:

"Where the spirit does not work with the hand, there is no art." - Leonardo da Vinci
 
Calculating infiltration is more art than science and depends greatly on the type and quality of construction; also a factor is the age of the building. It is also important to know that it is impossible to balance air flows to the design values perfectly. To accommodate this tolerance, it is common practice to provide 10-25% more air into a space than is exhausted to ensure the building is positive to the outside at all times.

In your scenario with the cafeteria, code requires so much OA that to not have an EF would create over-pressure problems. Such problems include whistling doors/windows, doors that never close/'heavy' doors (depending on swing), or doors that fly open.

It is likely the RA was calculated to provide about 10% positive pressure, then EA selected to match an EF's curve, finally RA recomputed to provide balance. You really need to ask your designer his thought process on how he came up with the exact numbers.
 
We usually allow about 0.05 CFM/SF or 100 CFM per door for pressurization.
Usually we want the pressurization to come from AHU/space around the cafeteria so if the cafeteria pressure is + the surrounding indoor areas would be ++ so food odors do not get transmitted to the other occupied spaces.
The air to the cafeteria should be transferred to the kitchen to provide makeup air to the kitchen hoods & dishwasher hood.
There should be control interlocks to vary the amount of outdoor air based on the hoods operating. The dishwasher hood should run all the time to avoid odor.
 
Status
Not open for further replies.
Back
Top