Hi,
This is wrt Hi-Z REF Protection.
The Phase CTs and Neutral CT parameters are same except the Rct Value. On Phase CTs the Rct(Ph) = 5 Ohm, On Neutral CT Rct(N) = 4 Ohm.
As the Rct Values are different there would be a Spill Current as the Dynamics are not Balanced.
1. Can I compensate for this Imbalance in the Stabilsing Resistor ?
2. If yes what is the factor , I should Compensate for?
3. Is it Advisable to go for Hi-Z REF for here ? As per the clients Specs Hi-Z REF is must.
Would appreciate All your valuable Inputs.
Thanks,