Hi,
I wonder if my setting of Variable speed drive need to be fined tune for Constant torque application.
Application: 10 HZ of 15 KW 4 Pole 50 Hz
Pump: Plunger triplex at 20 LPM
Pressure: 50 Bar achieved by regulating the throttle valve with gate valve
VFD; ATV 610D
Setting : only set for 25 KW parameter
From manufacturing the following is the
Estimate Power at rated 300 RPM 20 Hz is 3.6 GPM 50 bar is 2 Hp.
However running in my setup of new motor 15 KW connecting in Delta 415 V.
10 Hz, 25 Bar is already close to locked rotor current of 36 Amp wbich shown thr motor slowed down and stopped.
I pressumed the VFD setting ia not configured to Constant torque load where V/ Hz ratio is low.at 10 Hz voltage is aeound 40+ Volt. This reduced the torque which increased the current.
I wonder if my setting of Variable speed drive need to be fined tune for Constant torque application.
Application: 10 HZ of 15 KW 4 Pole 50 Hz
Pump: Plunger triplex at 20 LPM
Pressure: 50 Bar achieved by regulating the throttle valve with gate valve
VFD; ATV 610D
Setting : only set for 25 KW parameter
From manufacturing the following is the
Estimate Power at rated 300 RPM 20 Hz is 3.6 GPM 50 bar is 2 Hp.
However running in my setup of new motor 15 KW connecting in Delta 415 V.
10 Hz, 25 Bar is already close to locked rotor current of 36 Amp wbich shown thr motor slowed down and stopped.
I pressumed the VFD setting ia not configured to Constant torque load where V/ Hz ratio is low.at 10 Hz voltage is aeound 40+ Volt. This reduced the torque which increased the current.
the V/Hz ratio is too low, then the motor torque availability may not meet what is required and
the motor may experience a pull out condition. When pullout occurs, the motor will operate at high slip and potentially operate in the breakdown torque region, where the VFD will see high current and then
[end]
This video of the test
Hope anyone with great knowledge of VFD can enlighten me in the setting and caused of overload.
fault on overload