Pepwa33
Electrical
- Dec 5, 2019
- 4
Hi there,
I feel that I have a good grasp of the high impedance bus zone concept, however I am battling to understand one part of this.
Why do we assume the worst case is for an external fault where the CT closest to the fault saturates?
I understand why this CT saturates, as it will see the full summated secondary fault current. I can also appreciate that this secondary fault current will flow through the magnetising branch which acts as a short circuit instead of the CT windings. I also understand that the setting Voltage of the relay should be set above the voltage induced across this saturated branch (= N x Rleads + Rct x K).
What I don’t understand is if we consider the same CT summating all the fault current but WITHOUT saturation, then won’t there be the exact same current through the leads and CT resistance inducing the same voltage as the saturated CT scenario? Why do we consider the worst case for when the ‘CT is saturated’?
What am I missing? Is there some sort of back emf that opposes the voltage across the branch when the CT is unsaturated?
Edit: typo
I feel that I have a good grasp of the high impedance bus zone concept, however I am battling to understand one part of this.
Why do we assume the worst case is for an external fault where the CT closest to the fault saturates?
I understand why this CT saturates, as it will see the full summated secondary fault current. I can also appreciate that this secondary fault current will flow through the magnetising branch which acts as a short circuit instead of the CT windings. I also understand that the setting Voltage of the relay should be set above the voltage induced across this saturated branch (= N x Rleads + Rct x K).
What I don’t understand is if we consider the same CT summating all the fault current but WITHOUT saturation, then won’t there be the exact same current through the leads and CT resistance inducing the same voltage as the saturated CT scenario? Why do we consider the worst case for when the ‘CT is saturated’?
What am I missing? Is there some sort of back emf that opposes the voltage across the branch when the CT is unsaturated?
Edit: typo